What on earth do you mean by "serious amounts of excess energy"?
Some U.S A. measurements: (Halve or double to get 230 V values.)
100W 115V incandescent lamp: Cold 9.6 ohms Hot 132 ohms
Starting current ~ 12 A. Running current ~0.86 A
At least a dozen of these on a standard U.S. 15 A lighting circuit can
be turned on at once without tripping a 15 A branch circuit breaker.
The phenomenon of an MCB tripping when a filament bulb fails is well
documented and explained, it's nothing to do with "excess energy".
What happens is that when the filament breaks an arc is struck across
the ends. The arc has a low impedance and as the rest of the filament
burns away the arc ends up effectively shorting the circuit to the
lamp and the MCB trips. If the circuit is protected by a wire fuse
then the arc usually breaks before the fuse blows but MCBs (in the UK)
are fast enough to trip before the arc stops.
This sounds like a very plausible explanation. I have never seen this
happen on a U.S. circuit. Perhaps the lower voltage will not sustain
the arc long enough, or the gas ionization is different, or our 15 A
breakers aren't as fast as the MCBs.
Someone mentioned in-rush current to an ATX PC power supply. Most have
some form of input current limiting. There are two 480 mfd capacitors,
(typical), in series connected to the line through a rectifier. The
charging current would need to be limited. The ATX spec is vague on this.
Virg Wall
PS: I've worked in the UK with the USAirForce in UK MOD buildings
installing satellite tracking equipment. The only thing that bothered
me was remembering that UK switches are "up" in the "off" position.