W
w_tom
Impedance has little to do with the size of an AC electric
conductor. Anyone with an EE degree would have known that.
Impedance is determined by wire length, number of sharp bends,
wires splices, and other factors. Even though a 50' AC
electric wire is less than 0.2 ohms resistance, the same wire
would be about 120 ohms impedance to typically destructive
transients. Wire resistance between 6 AWG and 12 AWG is
major. Wire impedance between these two wires - trivial.
This is first year EE stuff.
Lets assumes Leythos $100 UPS will earth a trivial 100 amp
transient down that 50 foot wire (back to circuit breaker
box). Therefore the UPS is at less than 12,000 volts (100
amps times 120 ohms). Will that 100 amps travel down a 12,000
volt wire? Of course not. At 12,000 volts, the transient
will find other and destructive paths through adjacent
electronics. Again, this was old and well understood even in
the 1930s. I asked Leythos to describe how that UPS could
even provide protection because I suspect he did not even
understand why wire impedance dictates a 'less than 10 foot'
connection to earth ground.
Meanwhile, electronic appliances already have effective
internal protection. Protection that assumes a transient had
been earthed before entering the building. What does Leythos
forget to mention? That phone line already has a 'whole
house' protector installed by the telco. A protector so
inexpensive and so effective that the telco installs it for
free. A protector is only as effective as its earth ground. A
protector that made him think the UPS had provided the
protection.
Some foolishly think that wall receptacle safety ground is
earth ground. How with upwards of 130 ohms impedance in that
wire? Wire impedance is just one of so many reasons
electrical why plug-in protector are not effective AND why the
'whole house' protector (that costs tens of times less money
per protected appliance) is so effective.
In the meantime, if his UPS was earthing transients, then
that ground wire bundled with other wires would induce
transients on those other wires and other household
appliances. What kind of protection is that? Induced
transients: one more reason why his UPS is not effective. The
earthing wire also must be routed separate from other wires.
Just another reason why 'whole house' protectors are so
effective.
Leythos says his home meets 1972 code. But does it meet
post 1990 code? A house only meeting 1972 code may not have
sufficient earthing. Again, even a 'whole house' protector is
only as effective as its earth ground. Not the safety ground
that Leythos confuses with earth ground - due to lack of
pragmatic experience tempered by the principles. Homes built
in 1972 may still require earthing enhancements (upgrades to
the 1990 code) so that a 'whole house' protector can be
effective. We do earthing because protection has always been
about protection even from direct lightning strikes.
Again appliances contain internal protection. But those
typically destructive transients such as lightning are the
primary purpose of protectors and earthing. Earth the
destructive transient so that internal appliance protection is
not overwhelmed. Damage even from direct lightning strikes
need not occur.
So what does that UPS claim to accomplish? What already
exists inside appliances makes that UPS protector
ineffective. But then an adjacent protector can even
contribute to damage of the appliance, especially if the
'whole house' protector and proper earthing is not installed.
Don't start with this bottom posting nonsense. I post to be
easier to read as called for by RFC1885. This post conforms
to those standards. I have no interest in authoritarian
imposing bottom posting dictatorship so that posts are harder
to follow. Just like in those IEEE papers that EEs routinely
read - the new information is on top. Any reference to
previous posts, citations, bibliographies, and footnotes at at
the bottom - if someone need them. Should you choose to post
harder to read, then so be it. Its your choice. Top posters
are flexible and pragmatic - and don't make these silly
intolerant complaint that bottom poster do. I also don't
criticized you for foolishly believing the myths promoted by
APC. But that changes when you promote the lies and myth
from APC and from a perversion of RFC1885 upon others. But
again, you are doing the complaining while I am citing the
standards. RFC1885.
That UPS has all but no earth ground. It did not provide
the protection you speculated. But then the telco provided
'whole house' protector - that would have provided the
protection. Why? Fundamental fact: the protector is only as
effective as its earth ground. 120 ohms impedance? That
protector had all but no earth ground. No earth ground means
no effective protection. Numbers provided above demonstrate
that fact.
You disagree? Put up impedance numbers for that 6 AWG and
12 AWG wire. How many posts later and you still provide no
numbers to even demonstrate 1st year EE knowledge. And still
no way around this fact: the protector is only as effective as
its earth ground - and connection to that ground. The all so
standard 'less than 10 foot' connection.
conductor. Anyone with an EE degree would have known that.
Impedance is determined by wire length, number of sharp bends,
wires splices, and other factors. Even though a 50' AC
electric wire is less than 0.2 ohms resistance, the same wire
would be about 120 ohms impedance to typically destructive
transients. Wire resistance between 6 AWG and 12 AWG is
major. Wire impedance between these two wires - trivial.
This is first year EE stuff.
Lets assumes Leythos $100 UPS will earth a trivial 100 amp
transient down that 50 foot wire (back to circuit breaker
box). Therefore the UPS is at less than 12,000 volts (100
amps times 120 ohms). Will that 100 amps travel down a 12,000
volt wire? Of course not. At 12,000 volts, the transient
will find other and destructive paths through adjacent
electronics. Again, this was old and well understood even in
the 1930s. I asked Leythos to describe how that UPS could
even provide protection because I suspect he did not even
understand why wire impedance dictates a 'less than 10 foot'
connection to earth ground.
Meanwhile, electronic appliances already have effective
internal protection. Protection that assumes a transient had
been earthed before entering the building. What does Leythos
forget to mention? That phone line already has a 'whole
house' protector installed by the telco. A protector so
inexpensive and so effective that the telco installs it for
free. A protector is only as effective as its earth ground. A
protector that made him think the UPS had provided the
protection.
Some foolishly think that wall receptacle safety ground is
earth ground. How with upwards of 130 ohms impedance in that
wire? Wire impedance is just one of so many reasons
electrical why plug-in protector are not effective AND why the
'whole house' protector (that costs tens of times less money
per protected appliance) is so effective.
In the meantime, if his UPS was earthing transients, then
that ground wire bundled with other wires would induce
transients on those other wires and other household
appliances. What kind of protection is that? Induced
transients: one more reason why his UPS is not effective. The
earthing wire also must be routed separate from other wires.
Just another reason why 'whole house' protectors are so
effective.
Leythos says his home meets 1972 code. But does it meet
post 1990 code? A house only meeting 1972 code may not have
sufficient earthing. Again, even a 'whole house' protector is
only as effective as its earth ground. Not the safety ground
that Leythos confuses with earth ground - due to lack of
pragmatic experience tempered by the principles. Homes built
in 1972 may still require earthing enhancements (upgrades to
the 1990 code) so that a 'whole house' protector can be
effective. We do earthing because protection has always been
about protection even from direct lightning strikes.
Again appliances contain internal protection. But those
typically destructive transients such as lightning are the
primary purpose of protectors and earthing. Earth the
destructive transient so that internal appliance protection is
not overwhelmed. Damage even from direct lightning strikes
need not occur.
So what does that UPS claim to accomplish? What already
exists inside appliances makes that UPS protector
ineffective. But then an adjacent protector can even
contribute to damage of the appliance, especially if the
'whole house' protector and proper earthing is not installed.
Don't start with this bottom posting nonsense. I post to be
easier to read as called for by RFC1885. This post conforms
to those standards. I have no interest in authoritarian
imposing bottom posting dictatorship so that posts are harder
to follow. Just like in those IEEE papers that EEs routinely
read - the new information is on top. Any reference to
previous posts, citations, bibliographies, and footnotes at at
the bottom - if someone need them. Should you choose to post
harder to read, then so be it. Its your choice. Top posters
are flexible and pragmatic - and don't make these silly
intolerant complaint that bottom poster do. I also don't
criticized you for foolishly believing the myths promoted by
APC. But that changes when you promote the lies and myth
from APC and from a perversion of RFC1885 upon others. But
again, you are doing the complaining while I am citing the
standards. RFC1885.
That UPS has all but no earth ground. It did not provide
the protection you speculated. But then the telco provided
'whole house' protector - that would have provided the
protection. Why? Fundamental fact: the protector is only as
effective as its earth ground. 120 ohms impedance? That
protector had all but no earth ground. No earth ground means
no effective protection. Numbers provided above demonstrate
that fact.
You disagree? Put up impedance numbers for that 6 AWG and
12 AWG wire. How many posts later and you still provide no
numbers to even demonstrate 1st year EE knowledge. And still
no way around this fact: the protector is only as effective as
its earth ground - and connection to that ground. The all so
standard 'less than 10 foot' connection.