UPS unit needed for the P4C800E-Deluxe

J

jimbo

What is a good uninterruptible power supply unit for the Asus P4800E-Deluxe.
I want to pick up a good one and avoid frying my P4 3.2 and other components
during the many summer brownouts around here.
I have 8 hard drives, 2 dvd drives and a 5550W PS.

Jimbo
 
M

Mercury

First, there are 3 major classes of "SOHO" UPS.

1. Basic - a relay is used to switch to standby when the power fails.
Minimal if any protection against surges, none against bown outs (voltage
droops).
Here, the mains powers a battery charger when needed and flows straight to
the computer normally - surges will run straight through unless there are
surge suppressors added in the design. When a fail occurs, the relay simply
switches in a power converter to run off the batteries. The time to switch
is critical - too slow and your computer will crash. The inverter is usually
crude - square wave output with poor power characteristics. Not really that
useful.

2. Better - faster switching. May have proper surge protection etc. Perhaps
sine wave output. These are a bit dearer than those above, but usually quite
less expensive than the next.

3. Best - Output power runs off the inverter full time. Mains powers battery
charger full time. Surges are suppressed, but if big may go into the charger
and are further suppressed by it and the huge capacitance of the battery,
but excellent isolation as output runs through its own inverter from the
battery. These systems may have square wave output, but usually have sine
wave and better quality output. Most expensive, but best to get. These UPS
tend to have excellent surge and brown out suppression with no switch time
problems since there is no switching.

A good fast switching UPS is fine for many situations, but if you want peace
of mind then get the True Online type. Often the Square vs. Sine wave output
just doesn't matter too much. Avoid running peripherals of a UPS you just do
not need in a power fail scenarion - Printers, possibly Monitors, consider
LCD monitors for lower power consumption ==> better run time.

Do not trust cheapo surge suppressors - many have a life of ONE surge! Get a
lightning rod if you are in a risky area, and do not forget about surges
through telco lines.(sisters house got hit by a strike on teleco lines down
the road).

It is the Back up ability (run time at full rated load or run time at the
load you have) , Surge and Brown Out along with Switch speeds (for non True
Online UPS) that are the measures to be satisfied with. If in doubt, test on
your computer - simulate several power failures and check the PC stays up.

Take manufacturers claims with a grain of salt - use google and check
reviews. There are many 'domestic retail' el-cheapo brands that I would not
touch ever. Be picky & research.

Make sure you get a big enough UPS - I usually size them to use no more
than 60% of power rating (real ratings). IE buy 1.5 x or more than what your
computer needs max.

Make sure you get an auto shutdown interface & software. Google on what
people think of the s/w. Some is shyte. I have put in some MPC (? French)
ups recently & the s/w is really good as are the UPS. APC have been around
for a while. Some vendors web sites have online UPS calculators so give em a
go - they tend to over estimate a bit.

HTH
 
J

Jay T. Blocksom

What is a good uninterruptible power supply unit for the Asus
P4800E-Deluxe. I want to pick up a good one and avoid frying my P4 3.2 and
other components during the many summer brownouts around here.
[snip]

If poor-quality AC power (as opposed to simple power *failures*) is a concern
-- as well it should be -- then the *minimum* functionality you should accept
is what is commonly called "Line Interactive" (a marketing-ese term for
full-time voltage regulation, usually combined with some degree of noise
filtering and surge suppression). These types of units (such as the APC
"SmartUPS" series) are still "standby" supplies, in the strictest sense of
that term, since they still run the load off the AC mains under normal
circumstances and switch it to the inverter's output only if/when it senses a
serious power interruption; but they are nonetheless a HUGE improvement over
the rot-gut "Backup Power Supply" (as exemplified by the APC "BackUPS" and
"BackUPS Pro" series) which offer no significant degree of line conditioning.

Better still is a true on-line "double conversion" supply. These units use a
"bucket brigade" approach: The AC mains power is used *only* to run the
battery charger, which in turn constantly (re-)charges the batteries, which in
turn constantly power the inverter, which in turn *always* powers the load.
It should be intuitively obvious that this provides the greatest degree of
isolation between the power line (and the evils which lurk thereon) and the
protected equipment. In fact, this is the *only* type of unit which truly
deserves the term "Uninterruptable Power Supply". They used to be obscenely
expensive compared to similarly-sized line-interactive units, but that
situation is now much better... Decent double-conversion supplies can now be
had for perhaps 1.5-2X the typical line-interactive equivalent -- and IMCO,
they're worth every nickel.
I have 8 hard drives, 2 dvd drives and a 5550W PS.
[snip]

ITYM "550W". But that's still a fairly hefty load, as desktop PCs go,
especially if you're using a CRT-based monitor, as opposed to an LCD
(remember, you'll need to power the monitor off the UPS too, in order to be
able to interact with the system during a power failure -- if only to initiate
an orderly shutdown). So choose your UPS capacity accordingly. While a
650-700VA unit might be "adequate", something in the 1KVA range will likely be
your best bet. Besides, in this context, bigger is almost always better
anyway (in terms of run-time with a given load, if nothing else); so don't
scrimp.

--

Jay T. Blocksom
--------------------------------
Appropriate Technology, Inc.
usenet02[at]appropriate-tech.net

"They that can give up essential liberty to obtain a little temporary
safety deserve neither liberty nor safety."
-- Benjamin Franklin, Historical Review of Pennsylvania, 1759.
- - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - -
Unsolicited advertising sent to this domain is expressly prohibited under
47 USC S227 and State Law. Violators are subject to prosecution.
 
W

w_tom

A UPS from Mercury's first group is more than sufficient for
a computer. In fact, that "when a fail occurs, the relay
simply switches in a power converter to run off the batteries"
type UPS is also called a "computer grade" UPS. Those other
'group 3' UPSes cost on the order of $500+ to provide nothing
useful.

Learn what a power supply does. First 120 VAC passes
through line filters. Then 120 VAC is converted to 300 volts
DC. Virtually all noise, spikes, and surges are eliminated.
But your power supply provides more layers of protection. An
oscillator converts that hundreds of volts DC to an AC
voltage. Then voltage is filtered through a transformer -
galvanic isolation. The transformer output is again converted
to DC. Then that DC output is filtered but again. Then an
overvoltage protection circuit further eliminates excessive
spikes and noise. With so many layers of protection standard
in power supplies, then what does a UPS do? Typical UPS
provides less protection than what already exists inside a
standard power supply - even 30 years ago.

Those who recommend UPSes don't even discuss all this
existing protection and often don't even know what a power
supply does.

Those standard layers of protection in a power supply is
even why a square wave output (power that can harm some small
electric motors and power strip protectors) still does not
harm a computer. Computer power supplies are that resilient -
assuming a bean counter did not select the supply.

After so much hype about UPS protection, the bottom line
remains: a UPS only protects data from blackouts and
brownouts. Anything on power cord that protects hardware is
required and already inside that power supply. Look at those
so many layers of protection.

But power supply does even MORE. A power supply must
provide 100% power to every computer peripheral even when AC
mains voltage drops so low that incandescent lamps are at only
40% intensity. Brownout is also called a voltage sag. Just
another little fact that was standard even 30 years ago, and
yet routinely forgotten today to hype UPSes. That UPS is for
extreme brownouts (sags) and blackouts (no voltage).

Does that UPSes provide better surge protection? We always
demand numbers. The entire surge protection circuit is
measured in joules. How many joules in that UPS? Identical
circuit is also inside power strip protectors. Some
undersized power strip protectors have even more joules.
Why? Don't take my word for it. Look up the joules number
yourself.

Others will forget to cite numbers when making protection
claims. Bottom line: claims about hardware protection from a
plug-in UPS are mythical. All UPSes claim surge protection.
Then forget to mention how little that protection really is.
Both UPS and power strip have same undersized protection
circuit - as measured by the same parameter - joules. Worse
still: any protector damaged by a surge is ineffective - a
waste of good money. There is no protection from a "have a
life of ONE surge" protector. Yet even less joules of
protection is provided by the UPS.

If a power strip or UPS claims to protect from a surge that
typically does not do damage, then why would they bother to
properly size the protector? Notice that some "one time and
throw away" power strip protectors may have more joules.
Joules is a ballpark measurement of protector life
expectancy. Ineffective protectors minimize joules to claim
protection. They tell half truths so that others will
*assume*. 'Hype' is the protection provided by plug-in
UPSes.

Switchover time for a UPS: If a UPS switched over to
batteries too slowly, then the computer power supply is
defective. Again, specs even from Intel say the power supply
must provide interrupted power to computer; even when the UPS
takes a longest time to switchover. Again, review those
numbers yourself. Don't take my word for it.

Where is the real weakness in computer protection?
Repeatedly, everything necessary to protect at the power cord
must be inside a computer's power supply. This assumes a
computer assembler had sufficient knowledge to buy the
minimally acceptable power supply. Assumes he was not a bean
counter. Many computer assemblers could not even comprehend
what Mercury posted let alone list essential power supply
functions standard even 30 years ago. And Mercury did not
even post useful numbers that intimidate many computer
assemblers.

Asian manufacturers discovered a lucrative market of
technically naive computer assemblers. They dump inferior
power supplies into this market for greater profit. A
minimally acceptable supply must provide a long list of
numerical specs (such as how long power can be interrupted).
A minimally acceptable power supply must also cost at least
$60 full retail. So instead, many hype a UPS to *fix* missing
power supply functions?

Again, all minimally acceptable power supplies include
essential functions to protect a motherboard. Any function
effective on the power cord must be inside that supply. But
the rare and typically destructive transient can overwhelm
this internal protection. IOW an electrically 'literate'
computer expert appreciates why a less expensive and so
necessary 'whole house' protector, as part of a protection
'system', protects a computer. Again, that plug-in UPS
provides no such protection AND obviously cannot. The UPS has
no critically necessary 'less than 10 foot' connection to
earth ground. This alone indicates a glaring deficiency. So
instead, they even forget to mention the typically destructive
transient.

In summary: For effective protection of computer components
so that even a power supply failure does not damage
motherboard, disk drive, Ram, etc; the power supply must
contain functions that were even standard 30 years ago.
Functions so often missing in discounted power supplies.

For effective protection of data from blackouts and
brownouts, we install a plug-in UPS. Blackouts and brownouts
do not harm hardware - except where myths are widely promoted.

So that a typically destructive transient does not overwhelm
the computer's internal protection, we install and properly
earth a 'whole house' protector. It also protects other
appliances such as a clock radio, bathroom and kitchen GFCI,
smoke detector, dimmer switch, dishwasher and washing machine,
furnace controls, etc. Spend less money per appliance for
effective hardware protection. That means a minimally
sufficient power supply AND the 'whole house' protector.
$hundreds more for a UPS that provides no effective
motherboard protection? How does that make sense?
 
M

Mercury

I think you have a tad too much faith in the computer PSU.
The whole point of a good UPS is to remove doubt about the quality of power
available that would otherwise potentially damage the computer PSU.

Surges in the form of lightning are of such a huge potential magnitude that
some times the only solution is to unplug from the mains and move the
equipment away from conductors. I sometimes shutdown and pull the plug on my
own servers when a major electrical storm passes by.

It is the intermediate, unpredictable events that warrant UPS and surge
protection. The medium sized spikes that will fry the PSU and potentially
all the componentry in the computer. The power fails are the obvious
anomolies, as are the repeated failures. Continuity of service is only one
facit. ability to service is another.

I have come across some horrid scenarios: one a stock broker with 24 x 7
systems blown up because the earth wire was disconnected while attending to
an unrelated fault. There is no point in telling me what they did wrong - I
came in after the event.

Before all else, the purchaser really should try to understand what they are
buying, why, and why not buy it in a retail shop (how me a retailer that
sells good UPS). If the purchase is large then get and independant advisor
that knows his/her stuff.
 
W

w_tom

The $multi-million telephone switching computer also
disconnect with every approaching thunderstorm. Millions of
dollars connected to overhead wires everywhere in town. Since
effective protection from lightning is not possible, then they
must disconnect? OR, some people recommend ineffective UPSes
for lightning protection. Why does the telco provide service
during every lightning storm? Because 'whole house'
protection techniques are that effective. Protection that a
plug-in UPS cannot provide. I never unplug during
thunderstorms. I follow thunderstorms on the computer - in
real time. I don't worry about lightning damage because I
don't depend on mythical protection from a plug-in UPS.

By disparaging the protection inside a power supply, Mercury
then says UPS protection as even worse. Numbers were
provided. UPS has how few joules? Again, the numbers. Most
every UPS connects its load (the computer) directly to AC
mains when not in battery backup mode. How fast does that
UPS relay disconnect? Milliseconds. Meanwhile, destructive,
microsecond transients have long since done damage. 300
consecutive and destructive transients could pass through
before that UPS started to isolate the load. Where is the
protection? More damning numbers.

Yes, UPS claims protection. Then we look at the numbers.
Near zero protection is still protection. Just no effective.
And that is the point. Without numbers, then junk science
reasoning will claim UPS protection.

Any protection that works on the power cord is already
inside a power supply. One need only learn industry standard
numbers or read the long list of numeric specs (a hint for
identifying 'good' verses 'dumped' power supplies). Power
supplies contain effective protection. But that protection may
be overwhelmed by major transients (ie lightning). Transients
passes right through UPS - unimpeded. But a 'whole house'
protector earths before a destructive transient can overwhelm
the power supply. So what is a UPS doing? Battery backup in
case of blackouts or extreme brownouts - nothing more.

To claim otherwise, one must provide numbers. For example,
how many 'joules' inside a plug-in UPS? Mercury did not even
provide that number. Where is the earth ground? No earth
ground means no effective protection. Mercury also does not
even mention earthing. Why does that plug-in UPS also avoid
discussing earthing?

Many previously posted reasons demonstrated that UPS does
not provide effective protection. Insufficient joules.
Relay inside UPS cannot switch fast enough. Power supply
already has numerous layers of protection (starting with a
line filter and ending with an overvoltage protector) whereas
the UPS only connects that power supply direct to AC mains.
UPS output so 'dirty' that it may even damage electric motors
whereas computer power supply is so resilient as to even make
'dirty' UPS electricity irrelevant. Power supply must work
100% even when incandescent lamps are at only 40% intensity
(voltage sag or brownout). $100 for a UPS compared to $1 per
appliance for the effective 'whole house' protector.

A new reason why that UPS does not provide effective
protection. The destructive transient does not get to
motherboard through power supply (obviously). It uses the
green safety ground wire to bypass UPS; connects transient
direct to motherboard. Those recommending the UPS forget to
mention that UPS transient protector circuits (measured in
joules) shunt a destructive transient into that bypass wire.
What does that transient seek? Earth ground. The UPS
provides a new destructive path to earth via the motherboard -
the bypass wire. What kind of protection is that? Again,
ineffective. One more reason why the 'whole house' protector
is required and why the plug-in UPS is so ineffective.

Claims of UPS protection were made without numbers.
Mercury is encouraged to provide numbers. Start, for example,
with joules. Start, for example, with numbers listed in specs
from that UPS manufacturer. Why do UPS manufacturer specs
have so few numbers? They provide numbers they are required
to provide - such as joules. Their specifications completely
ignore another typically destructive transient so that
consumers will *assume* total protection. Missing numbers.
More damning facts.

The 'whole house' protector does provide protection from all
types of transients. A protector is only as effective as its
earth ground. 'Whole house' protectors are earthed; building
wide UPSes are earthed; plug-in UPSes are *not* earthed.
Furthermore, the 'whole house' protector also costs tens of
times less money.

We don't unplug for thunderstorms. We install effective
protection not found in plug-in UPSes. Protection defined by
the most critical protection system component: single point
earth ground. Effective protection inside a power supply is
not overwhelmed when properly earthed protector is installed.
 
M

Mercury

Reread my original post - in that I did not recommend the basic or
intermediate UPS's, only the true online type in which all power runs across
the battery which is isolated from the mains - somewhat - by the charger
circuit.

Where are you? US? Well earthing standards there are different to elsewhere.
Here it is illegal to have an incorrectly wired business or house & these
standards are enforced right thru to the earth wire to the UPS and computer
PSU. Last I knew, only double insulated devices were allowed to not have an
earth wire. These days RCD devices are common (but thats irrelevant). In the
AT computer days you were required here to be a certified electrician before
you could be employed servicing computers due to mains wiring and earthing
requirements.

Certainly the # of joules is important, but it is not as there is always
potential for a larger surge in which case that filter / PSU / UPS /
anything else is no use whatsoever. It comes down to what you can afford to
prepare for.

I always recommend lightning rods and prompt for double checks on the health
of building earth systems - they can get damaged and when they are it is too
late when you find out the hard way. (24x7 systems).

Invariably it comes down to regional probability, requirements, and budget +
Knowledge.

Again, I will state *not* to trust the computer PSU from an electrical surge
perspective. Don't forget that a switch mode PSU is like a tight rope
walker - all is hunky dory so long as there isn't an earthquake. Computer
PSU's are the most fallable part of acomputer next to the HDD. taking 110 or
230v, rectifying it, bunging it through a high voltage / high frequency
transister osicillatorinto a compact torroidal transformer, then 'dumping'
out often raw power via a simple diode / capacitor / sometimes inductor
circuit is crude, however there is a lot of complexity in the controller
electronics as you no doubt know - providing a feedback loop that is
responsive while catering for short circuits etc. is actually one of the
most overlooked examples of (usually) quality design, construction, and
componentry. With all this advanced design and in reality great variety in
quality of performance, I *would not* put any more trust into a computer PSU
than risks indicate one should ! Actually there is no room for trust...

I have read many stats on Computer PSU's but never noticed mention of surge
protection - joules or not.
 
W

w_tom

Recommend the $500 UPS to solve what a $1 per appliance
solution does? Again, even the green bypass wire makes the
"true online type" UPS ineffective. Destructive transient
bypasses the UPS. Just one of so many reasons why a plug-in
UPS is not effective.

What does that UPS do that the power supply does not?
Nothing. The plug-in UPS does not even claim those 1000+
volts isolation. Power supplies must withstand 1000+ volts as
even required by industry and Intel specs. Robust protection
inside a power supply - that still requires a 'whole house'
protector. $500 for a true online type UPS provides no
additional protection. $500 and the 'whole house' protector
is still necessary? What kind of protection is that?
Mythical.

An eleventh reason why that true online type UPS is not
effective. Is that plug-in UPS going to stop, block, or
absorb what miles of sky could not? Are silly one inch parts
(those parts that are woefully undersized; too few joules)
going to stop what miles of air could not? Of course not.
And yet 'somehow' a true online type UPS does just that?
Nonsense. How many more reasons demonstrate what that UPS
specification also says by omission. It does not provide
effective transient protection.

No earth ground means no effective protection - everywhere
on earth. Even the true online UPS is not earthed (safety
ground is electrically different from earthing; why the number
'less than 10 foot' is important). Therefore 'true online
type' does not claim to protect from the typically destructive
transient. Obviously. Protection is only as effective as that
earthing connection. How many more reasons need be posted?

Again, no numbers to demonstrate claims for this true online
type UPS. No numbers means junk science reasoning. That
UPS provides mythical hardware protection. Protection must
factually exist. That means numbers. That also means
earthing. "True online type" does not even discuss earthing -
for good reason.

How many joules in that "true online type" UPS? Never
provided. $500 for ineffective protection - or $1 per for
effective protection from a 'whole house' protector. Which
makes more sense? Numbers again are damning.
 
M

Michael W. Ryder

w_tom said:
Recommend the $500 UPS to solve what a $1 per appliance
solution does? Again, even the green bypass wire makes the
"true online type" UPS ineffective. Destructive transient
bypasses the UPS. Just one of so many reasons why a plug-in
UPS is not effective.

And exactly how does your "miracle" $1 part allow my computer to keep
working 30 minutes after the local grid goes down? UPS systems are not
bought to make the power going into the computer "safe", but to allow
the computer to keep working even when the power grid is not.

What does that UPS do that the power supply does not?
Nothing. The plug-in UPS does not even claim those 1000+
volts isolation. Power supplies must withstand 1000+ volts as
even required by industry and Intel specs. Robust protection
inside a power supply - that still requires a 'whole house'
protector. $500 for a true online type UPS provides no
additional protection. $500 and the 'whole house' protector
is still necessary? What kind of protection is that?
Mythical.

And how often do power supplies die in a puff of smoke? Far more often
than your theoretical claims would have it. If they were so well built
they would never fail, there would be no heartbreak of psoriasis, etc.

<snip further rantings>
 
H

H.W. Stockman

w_tom said:
Recommend the $500 UPS to solve what a $1 per appliance
solution does? Again, even the green bypass wire makes the
"true online type" UPS ineffective. Destructive transient
bypasses the UPS. Just one of so many reasons why a plug-in
UPS is not effective.

What does that UPS do that the power supply does not?
Nothing. The plug-in UPS does not even claim those 1000+
volts isolation. Power supplies must withstand 1000+ volts as
even required by industry and Intel specs. Robust protection
inside a power supply - that still requires a 'whole house'
protector. $500 for a true online type UPS provides no
additional protection. $500 and the 'whole house' protector
is still necessary? What kind of protection is that?
Mythical.
I'm pretty sure I remember you from a similar discussion 3 or 4 years back.

Serious questions: could you provide references, for those in the US 1) that
give a quantitative analysis of you r summary of plug-in surge-protector
performance? 2) That give a summary of whole-house surge protection?

I looked into the latter years back, and found nothing -- no companies that
offered a solution, and local electricians seemed puzzled by inquiries.
Perhaps I just didn't know the correct terms. The few on-line references I
found were light on science, and high on innuendo and supercilious
condemnation.

Like others, I'm mainly interested in a UPS ability to switch to emergency
power when the grid goes down. The surge protection part of the UPS is
fairly cheap, comppared to the power protection. I also surge-protect the
lines that go through my attic and connect distant PCs, because some have
the view that secondary induction of current in such lines is probably more
common than desttruction from direct lightning hits.
 
M

Mercury

<snip>

What is the "a $1 per appliance solution" solution?

Not all UPS of a given type are created equal. That is why it is so
important to thoroughly understand what each specific model does and does
not do along with what you should have to meet requirements.

There is some real crap out there with UPS - hence my statement not to buy
from a retailer.
 
W

w_tom

If you think a surge protector somewhere in the line
provides protection, then you are assuming the protector is
stopping, blocking, or absorbing surges. IOW they got you to
worship the myth.

Another myth are all those other interior surges from
refrigerator, etc. If they existed, then we all trooped weekly
the the hardware store to replace dimmer switches and GFCIs -
even before the PC existed. Why did those transients not
exist then and now exist? Myths. And again, any such
transient is made completely irrelevant by protection already
inside the appliance. Only the 'earthquake' type surges
overwhelm internal protection - which is why the 'whole house'
protector is so effective. Which is why the 'whole house'
protector is even installed, for free, by your telco where
their wire enters your building.

You asked for sources. Today's reading is but a sampling.
'Today' because you may be reading all day.

A benchmark in protection is Polyphaser. Notice their app
notes don't discuss a product line. Polyphaser is about real
protection. They discuss earthing - extensively:
http://www.polyphaser.com/ppc_ptd_home.aspx
Another real world provider of hardware protection also
provides extensive app notes:
http://www.mtlsurgetechnologies.com/downloads/tans/index.htm
This figure from an industry professional demonstrates the
concept. Note that destructive transients enter even via
underground wires. Each of two structures has it own single
point earth ground:

http://www.erico.com/erico_public/pdf/fep/TechNotes/Tncr002.pdf
And a more complex technical paper with numbers:

http://www.erico.com/public/library/fep/technotes/tnfep6ppa.pdf
A second paper that is easier for laymen to read:

http://www.erico.com/public/library/fep/technotes/tnfep6pp98.pdf

A utility provides further description of basic concepts:
(the bad, ugly and good, left to right)
http://www.cinergy.com/surge/ttip08.htm

Figure from the National Institute of Standards and
Technology demonstrate how multiple earthing points would
contribute to damage of a fax machine:
http://www.epri-peac.com/tutorials/sol01tut.html
Another from Polyphaser demonstrates same type damage from an
incoming buried wire:
http://www.polyphaser.com/ppc_PEN1028.asp
Lightning strikes somewhere across the street close to the
below grade West cable vault. ... The first line of defense
is the telco protection panel, but the panel must be connected
to a low resistance / inductance ground. There was no adequate
ground available in the telephone room.



Examples of numerous earthing methods so that cell phone
electronics routinely suffer direct lightning strike without
damage:
(see ground network on page 14)
http://www.leminstruments.com/pdf/LEGP.pdf

http://www.leviton.com/pdfs/spdrefman/spdrefman.pdf
Fundamentals on Lightning Protection Grounding and Surge
Suppression
http://members.cox.net/pc-usa/station/grounding.htm
http://members.cox.net/pc-usa/station/basics.htm
http://members.cox.net/pc-usa/station/ground3.htm

Some testimony from industry professionals with extensive
experience:
http://www.telebyteusa.com/primer/ch6.htm
See Section 6.4: WHEN SHOULD YOU WORRY ABOUT LIGHTNING?
Conceptually, lightning protection devices are switches to
ground. Once a threatening surge is detected, a lightning
protection device grounds the incoming signal connection
point of the equipment being protected. Thus, redirecting
the threatening surge on a path-of-least resistance
(impedance) to ground where it is absorbed.
Any lightning protection device must be composed of two
"subsystems," a switch which is essentially some type of
switching circuitry and a good ground connection-to allo
dissipation of the surge energy.
http://www.harvardrepeater.org/news/lightning.html
Well I assert, from personal and broadcast experience spanning
30 years, that you can design a system that will handle *direct
lightning strikes* on a routine basis. It takes some planning
and careful layout, but it's not hard, nor is it overly
expensive. At WXIA-TV, my other job, we take direct lightning
strikes nearly every time there's a thunderstorm. Our downtime
from such strikes is almost non-existant. The last time we
went down from a strike, it was due to a strike on the power
company's lines knocking *them* out, ...
Since my disasterous strike, I've been campaigning vigorously
to educate amateurs that you *can* avoid damage from direct
strikes. The belief that there's no protection from direct
strike damage is *myth*. ...
The keys to effective lightning protection are surprisingly
simple, and surprisingly less than obvious. Of course you
*must* have a single point ground system that eliminates all
ground loops. And you must present a low *impedance* path for
the energy to go. That's most generally a low *inductance*
path rather than just a low ohm DC path.

Sun Microsystems also describes this widely understood
concept (except here where those without numbers would instead
attack this poster):
Planning guide for Sun Server room
Section 5.4.7 Lightning Protection (Adobe page 89):
http://www.sun.com/servers/white-papers/dc-planning-guide.pdf
Lightning surges cannot be stopped, but they can be diverted.
The plans for the data center should be thoroughly reviewed to
identify any paths for surge entry into the data center. Surge
arrestors can be designed into the system to help mitigate the
potential for lightning damage within the data center. These
should divert the power of the surge by providing a path to
ground for the surge energy. Protection should be placed on
both the primary and secondary side of the service transformer.
It is also necessary to protect against surges through the
communications lines. The specific design of the lightning
protection system for the data center will be dependent on the
design of the building and utilities and existing protection
measures.


Above discuss the secondary protection system. Homeowner
must also inspect his primary protection system:
http://www.tvtower.com/fpl.html

Electronic transient damage is typically from external
events. In simpler terms, every wire entering the appliance
is connected to a large 'antenna' system that is also on
utility poles. Those AC utility and telephone wires are no
different than antennas connected to communication system
(when discussing protection). And so we learn from those who
most often suffer direct strikes without transistor damage.
Some testimonies on protection effectiveness and the
principles that make transistor protection effective:
http://scott-inc.com/html/ufer.htm
http://www.psihq.com/iread/ufergrnd.htm

http://www.eham.net/articles/6848?ehamsid=61915ecd56a94ff1e861e080ac23c416
Electrical Code vs. Good RF Grounding by K9KJM on 22
November 22 2003
Those who say "nothing will withstand a direct lightning strike"
are very misinformed. My towers take direct lightning hits most
every big storm. So do most all tall commercial towers. With NO
damage!

Another electrical engineer who I am told is highly regarded
in the stereo industry:

http://www.svconline.com/mag/avinstall_surge_protectionthe_enemy/
The real problem is the haphazard use of common all-mode
protectors at AC outlets or outlet strips. In many cases, this
practice causes either system noise problems or hardware damage.
... The hardware damage does not usually occur in the power
supply, where you would expect it, but in the signal I/O
interfaces that connect to the outside world.
...
the ground wires may be quite long. Most transient over-voltages
are high-frequency events, having most of their energy well
above 100 kHz. At these frequencies, long wires, regardless of
their gauge, have high impedance and will develop extremely high
voltage drops when carrying the high current pulses created by
MOV clamping. ... This voltage is likely to reduce interface
circuitry in the computer, printer or both to silicon vapor.
More frequent low-voltage spikes (down to the low-current MOV
clamp of 300 V or so) will still cause high-current pulses to
flow in the same loop. These smaller noise spikes between the
grounds will cause errors or lockup.
...
The absolute best place to guard against incoming spikes and
surges is at the service entry panel or a sub-panel that
powers everything in an interconnected system.

Too many go to 'hyped' surge protector and UPS companies to
find facts. You know their names. The only (and completely
ineffective) protectors sold in Staples, Sears, Office Max,
K-Mart, Target, Radio Shack, Circuit City, Best Buy, and
Wal-Mart will not provide technical facts about protection.
They are selling protectors that effectively have NO earth
ground connection. I have simply provided a scattering of
real world sources. Let me know if you want tomorrow's
reading. Notice the person who has sources also posted
numbers. But then the person who posts reality in
confrontation to popular myth - the naive will always believe
myths over numbers.

In the meantime, electricians will often be puzzled. They
know what code requires and little about why. Electricians
are only technicians. They only need know code requirements
for human safety. There is no requirement for transistor
safety. We still build new homes as if the transistor did not
exist. Concepts of wire *impedance* are as completely foreign
to electricians as to some here who recommend a plug-in UPS.
Electricians are concerned with wire *resistance*. Surge
protection is about wire *impedance* and about earthing beyond
what is required by code (beyond what electricians need
know). So yes, electricians are not knowledgeable sources and
will not be until we have codes requiring transistor
protection.

Surprisingly, the cable companies recently began teaching
their installers the simple concepts of transistor safety.
And yet still I heard about one who 'earthed' the cable in a
porch flower box.

Real world protectors are sold by serious electrical
manufacturers - Square D, GE, Leviton, Intermatic, Cutler
Hammer, Siemens, Furse, etc. 'Whole house' protectors from
some above manufacturers are sold in better stores such as
Home Depot and Lowes. Effective protection for about $1 per
protected appliance. Protection based upon principles
provided above - and in tomorrow's reading list should you be
interested.

Just more answers about protecting that motherboard. Those
plug-in manufacturers will discuss nothing that harms their
'sales based upon half truths'. In the real world, protection
is only as effective as the earth ground. To others,
protection is only found in the first product promoted by
propaganda.

It is blunt. Some may be insulted. But honesty (not
political correctness) is the point of this post.
 
W

w_tom

How many times need I post about 'whole house' protectors.
And finally you ask about "a $1 per appliance solution"?
Where have you been. A sampling of facts is provided in a
reply to H. W. Stockman. In that reply are numerous examples
of effective protection - no UPS solutions exist. As I have
been saying all along, you first need learn some of the basic
electrical principles involved in protection. Some of those
citations to H. W. Stockman will be too complex - too much
advanced math. Others will be more readable for laymen.
Provided is everything from the technical concepts to laymen's
diagrams. Much of what is provided by industry professionals
will be both new and quite informative for you.

Also listed were providers of "$1 per protected appliance"
solutions and where they can even be obtained retail. Look
for the paragraph that include the list of serious
manufacturers:
... Square D, GE, Leviton, Intermatic, Cutler Hammer,
Siemens, Furse, etc.

When it comes to surge protection, plug-in UPSes are created
equal. They use the same protection circuit found in power
strip protectors.

Now for a benchmark. How to identify the ineffective
protector:
1) No dedicated connection for the 'less than 10 foot'
conductor to single point earth ground, AND
2) manufacturer avoids all mention of earth ground.

After all, as those so many industry professional (even Sun
Microsystems) note in that H. W. Stockton post: a surge
protector is only as effective as its earth ground. No earth
ground means no effective protection. There is no way around
this principle demonstrated even by Ben Franklin in 1752.
 
J

Jay T. Blocksom

A UPS from Mercury's first group is more than sufficient for
a computer.
[snip]

Maybe for *your* computer(s), but certainly not for mine.

The el-cheapo standby-type supplies that "Mercury" (rather charitably)
described as "Basic" offer only minimal "protection" against the simplest (and
rarest) types of total power failures, and little else. They can do
absolutely nothing about the (often abysmal) *quality* of the power coming out
your wall outlet. Hence, their ability to shield the load from the plethora
of short-term fluctuations (so-called "brownouts", noise, frequency and
waveform aberrations, etc.) that have become increasingly common as power
utilities scrimp ever more on their QOS (and chronically fail to ensure that
generating capacity keeps pace with demand) is sorely lacking. The worst of
them also often throw all sorts of self-generated noise onto the line (and
into the air), which can (and does) interfere with the operation of *other*
equipment (especially RF-based equipment, such as a wireless LAN -- or your TV
set).
In fact, that "when a fail occurs, the relay
simply switches in a power converter to run off the batteries"
type UPS is also called a "computer grade" UPS.
[snip]

Only by the marketing mavens trying to sell then to the Great Unwashed, and
the gullible fools who have bought into their line of bull.
Those other
'group 3' UPSes cost on the order of $500+ to provide nothing
useful.
[snip]

This is flat-out wrong.

A proper double-conversion UPS will offer MANY advantages over the various
low-end pieces. Among these are effective isolation between the load and the
line, true sine-wave output with minimal THD (sometimes also provided by the
better line-interactive units, but definitely not by the low-end standby
supplies you claim above to be "more than sufficient"), more robust batteries
and inverters (they _have_to_ be beefier, as they are in use all the time as
opposed to "just occasionally") and usually better build quality in general.

As for cost... Well, that can (and will) be all over the map, depending on
the manufacturer, the vendor, and especially the load capacity. You can spend
a few hundred, or you can spend several thousand -- but this also applies, to
very nearly the same degree, to standby & line-interactive models. As I
stated in my earlier article, a proper double-conversion UPS will generally
cost something on the order of 1.5-2X what an equivalent line-interactive
model will run. Here are a few examples for units in the 1KVA range (which
would be quite adequate for the OP's application):

TRIPP LITE OMNI SMART 1050VA
(Line Interactive / Stepped-square output) $277.95
<http://www.axiontech.com/prdt.php?item=34427&PRICECOMPARISONSID=7010b72b1aad24a0238d7ba547832d20>
TRIPP LITE SU1000XL
(Double Conversion / Sine-wave output) $413.95
<http://www.axiontech.com/prdt.php?item=61114&PRICECOMPARISONSID=7010b72b1aad24a0238d7ba547832d20>

The latter is exactly 1.489296636086 times as expensive as the former.

Para Systems Minuteman SmartSine S1000
(Line Interactive / Sine-wave output) $325.
<http://www.bisonbusiness.com/mis1fcoshcos.html>
Para Systems Minuteman MCP 1000 E
(Double Conversion / Sine-wave output) $525
<http://www.bisonbusiness.com/mimcfcoshcou.html>

The latter is exactly 1.615384615385 times as expensive as the former.

And finally, both from <http://www.battery-usa.com/Powercom-UPS.htm>:

PowerCom HOME-1000A
(Line Interactive / Sine-wave output) $281.33
PowerCom ULT-1000
(Double Conversion / Sine-wave output) $456.00

The latter is exactly 1.620872285217 times as expensive as the former.

Please note that I am *NOT* specifically recommending any of these particular
models, vendors, etc.; I'm just using them as handy examples.
Learn what a power supply does.
[snip]

You should take your own advice. Your description which follows is seriously
flawed in several ways (at least presuming you're talking about the typical
"switching" type PC power supply unit).
First 120 VAC passes
through line filters.
[snip]

Maybe, but most often not. For the current to "pass through" a filter, that
filter must be composed (at least primarily) of inductive components (i.e., a
choke). But chokes are relatively expensive and bulky; and they don't do much
for you in a true AC environment. So typically, MOVs and bypass capacitors
are used instead. The current does not "pass through" these components (tho'
it might be said to "pass by" them).
Then 120 VAC is converted to 300 volts
DC.
[snip]

Uhhh... no.

It is rectified, usually (or at least hopefully) by a full-wave bridge
rectifier circuit. This produces a (very rough and noisy) pseudo-DC output of
approximately 180V.
Virtually all noise, spikes, and surges are eliminated.
[snip]

Not even close!

Have you ever looked at the waveform output from one of those line-AC
rectifier circuits on a 'scope? I thought not. As noted above, at this stage
in the circuit, that waveform is *extremely* ragged and noisy (technically
referred to as "ripple") -- which is why the rectifier is (at least in any
half-decent supply) immediately followed up with more filtering caps (and
maybe even a small choke, this time, since the demands on it are so much less
after rectification).
But your power supply provides more layers of protection. An
oscillator converts that hundreds of volts DC to an AC
voltage.
[snip]

It is disingenuous at best to call that a "layer of protection". It is simply
a necessary part any switching-type power supply. And the reasons for it are
not to provide any better protection or "power quality" to the load. The
near-sole reason for this type of design is *cost* -- you need a LOT less iron
to transform high-frequency (typically 5KHz to 50KHz) AC than low- (i.e.,
line-) frequency AC (60 Hz in the U.S.); and the cost savings provided by
using a relatively tiny transformer (see the next step in this saga) much more
than offset the costs of the "preliminary" rectification/switching circuitry.
It also makes for a physically smaller and lighter PSU, which saves still more
money in manufacturing and shipping costs down the line.
Then voltage is filtered through a transformer -
galvanic isolation.
[snip]

<SPLORF!>

A transformer has *nothing* to do with "galvanic isolation", at least in this
context. And "galvanic isolation" in turn has *nothing* to do with protecting
a PC from power-line anomalies.

Do you even know what that term means? (Hint: Think corrosion. Or
batteries.)
The transformer output is again converted
to DC.
[snip]

Again, a simple rectifier circuit, which again produces a very rough and noisy
pseudo-DC output -- actually, several such rectifiers, producing several such
outputs, since the transformers used in PC PSUs necessarily have multiple
secondary windings/taps.
Then that DC output is filtered but again.
[snip]

Well, of course -- we've just made a ton of noise and other crap via the
rectification process, which we now need to dispose of. But this is S.O.P.
for *any* power supply, switching or linear, in a PC application or virtually
anything else.
Then an
overvoltage protection circuit further eliminates excessive
spikes and noise.
[snip]

Uhhh... No, again. You are presumably referring to active voltage
regulation, which any decent PSU (for virtually any application, not just PCs)
will provide. But this is (at least typically) not so much a matter of
"overvoltage protection" (or under-voltage, for that matter) as it is a means
of enabling the designer to scrimp on the final filtering caps and/or chokes.
With an adequately responsive AVR circuit to rely on, those filtering caps
and/or chokes don't need to be nearly as effective as would be necessary if
they were being counted on to provide *all* of the output filtering; hence,
they can be smaller and cheaper.

In reality, the actual "over-voltage protection" feature provided by some PC
PSUs works *against* data integrity, not for it, since it can (and will,
if/when it trips) arbitrarily shut down the PSU (requiring a AC-off cold
start) without warning.
With so many layers of protection standard
in power supplies, then what does a UPS do? Typical UPS
provides less protection than what already exists inside a
standard power supply - even 30 years ago.
[snip]

Thirty years ago, the "PC" had not yet been invented (tho' the first 8-bit
microprocessors had been developed, so the birth of the PC was imminent -- I
discount such "lunatic fringe" aberrations as the MITS Altair, which was
purely a hobbyist piece -- with a *linear* power supply, by the way), and
switching power supplies (in any application) were both relatively rare and
quite crude by today's standards. They were, quite justifiably, viewed as
rot-got el-cheapo substitutes for a "proper" linear power supply.

Yes, today's switching PSUs (at least the higher-quality ones) are much better
than those early travesties; but that's not the point.
After so much hype about UPS protection, the bottom line
remains: a UPS only protects data from blackouts and
brownouts. Anything on power cord that protects hardware is
required and already inside that power supply. Look at those
so many layers of protection.
[snip]

Nonsense.

*IF* we could count on both the quality and the reliability of the AC mains
power we use to feed these supplies, at least most of them would do an
admirable job of running the mobos, memory, CPUs, disk drives, etc., that your
typical PC is composed of. But we *cannot* count on that. In fact, that
situation is getting worse every day, for the reasons already touched on above
(blame the NIMBYs, if you want; but the fact remains -- we are facing an
electrical power crisis that will surely only get worse before it gets
better). Concurrently, we are becoming more and more dependant on our
electronics -- especially our computer systems -- for our day-to-day
activities and existence. That is a prescription for a very unpleasant
wake-up call, which we *will* get, sooner or later; but I digress.

Getting back to the point...

The "hold-up time" specs quoted for typical PC PSUs range from about 10ms to
perhaps 17ms -- i.e., one AC cycle _at_best_ -- and even these are "best case"
specs obtained under laboratory conditions. All manner of power-line
aberrations (besides simple "total failures") will have event durations which
exceed this threshold. So some sort of "upstream" protection is
near-mandatory, if you value your data.

The "switching time" specs for typical low-end standby-type "UPS"s are in the
several-millisecond range (tho' again, these are "best case" lab-conditions
specs). Now, you might think that, because these figures are significantly
lower than (typically about 1/4 - 1/2) the typical PSU "hold-up time", there's
no problem... But you'd be wrong. This is only the actual *switching* time,
which by definition only starts *after* a power-line disruption has been
sensed and the control circuit tripped -- IOW, by the time the "UPS" *starts*
to switch the load, the crap has *already* been fed through to the output.
In summary: For effective protection of computer components
so that even a power supply failure does not damage
motherboard, disk drive, Ram, etc; the power supply must
contain functions that were even standard 30 years ago.
Functions so often missing in discounted power supplies.
[snip]

Ah, ha! Perhaps this explains (at least in part) your apparent fundamental
misunderstanding of the issues. It's not about "protection of computer
components", all of which are virtually always easily replaceable. It *is*
about protection of your DATA -- which in any serious application is far more
valuable than all the hardware, software, peripherals, etc., put together.
For effective protection of data from blackouts and
brownouts, we install a plug-in UPS. Blackouts and brownouts
do not harm hardware - except where myths are widely promoted.
[snip]

But here you imply that any ol' "plug-in UPS" is equivalent to any other
"plug-in UPS" -- which is most assuredly *NOT* the case. (And BTW... You're
also dead wrong about blackouts/brownouts not being able to harm hardware; and
I have the fried A/V gear from both my shore home and my main residence to
prove it.)

This raises the question of just what axe you're attempting to grind.

Out of curiosity, I just took a quick look at some of your other recent
postings via Google Groups; and I must say... Your grossly simplistic (and in
some cases just-plain-wrong -- such as was exemplified in
<http://groups.google.co.uk/[email protected]>;
hint: the voltage output of a regulated power supply will hold up just fine
until *immediately* before it falls apart spectacularly -- hence, your "cure
all" DMM tells you NOTHING about reserve capacity) views on matters related to
power supplies and your apparent obsession with PSUs as the root cause of all
computer problems (even those rather obviously caused by software or "pilot
error") seems suspect, at best.

No one here (least of all me) is claiming that a (presumably decent-quality)
switching-type standby "UPS" is totally worthless; but to suggest that they
are the end-all and be-all of UPS design is both misleading and just plain
silly.

--

Jay T. Blocksom
--------------------------------
Appropriate Technology, Inc.
usenet02[at]appropriate-tech.net

"They that can give up essential liberty to obtain a little temporary
safety deserve neither liberty nor safety."
-- Benjamin Franklin, Historical Review of Pennsylvania, 1759.
- - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - -
Unsolicited advertising sent to this domain is expressly prohibited under
47 USC S227 and State Law. Violators are subject to prosecution.
 
W

w_tom

Correct. Double conversion would provide protection, but IF
a destructive transient was type of transient they claim to
protect from. A destructive longitudinal mode transient is
not seen by UPS battery and inverter as transient passes right
through UPS to damage computer. Transient that passes on both
sides of battery and inverter equally is Zero Volts - not seen
by battery, et al. Same transient can be thousands of volts
across a motherboard. This is EE101 stuff. Just another
problem with that 'speculated' UPS protection. It ignores
this destructive type of transient and basic EE principles.

Another significant problem. Wire that bypasses the UPS;
carries a destructive transient around UPS and directly into
motherboard. So many reasons why a group 3
(double-conversion) UPS provides ineffective protection. Of
course, these and other reasons were listed previously. Why
does Jay ignore numbers in previous posts to promote a $500
UPS as protection? And yes, the listed $500 UPSes are the
groups 3 UPSes. $500 and still does not even claim protection
from the destructive type of transient. The $275 versions do
less - and still don't claim such protection. Jay's post
even pretends other and destructive transients do not exist.

Moreso, protection cited in those groups 3 UPSes are already
inside the power supply - as it was 30 years ago. What a UPS
provides is nothing because the power supply already provides
it - as was accurately posted previously.

Further problems as cited in provious posts. That double
conversion protection may be overwhelmed by the typically
destructive transient that could also overwhelm protection
inside a power supply. $500 for protection that is equivalent
to what exists inside the power supply? What kind of
protection is that?

Protecting a UPS is but another reason why the 'whole house'
protector is essential. With a double conversion UPS, one
still requires a 'whole house protector. But with a 'whole
house' protector, that UPS is made unnecessary (since that
protection is already inside the power supply).

But again, first define the many types of transients. Jay
assumes only one type of transient - which that UPS
manufacturer hopes lurkers will do to promote their myth. The
transient that double conversion UPS does not protect from is
the transient that would damage a motherboard. To be
effective, a UPS must protect from a type of transient that it
does not even claim to protect from. Damning problem. The
UPS still required a 'whole house' protector. But if the
'whole house' protector is installed, then that UPS for
protection is not required.

One more point. A 'filter' function provided by double
conversion UPS is going to stop what three miles of sky could
not? Of course not. A destructive transient is a current
source. That means voltage will increase, as necessary, to
overwhelm filtering. As has been proven even before WWII and
has been demonstrated by Ben Franklin in 1752: destructive
transients are not stopped, blocked, or absorbed. That is
true everywhere except where these plug-in UPS myths are
promoted. Destructive transients are eliminated by earthing -
which the UPS must avoid discussing.

I can appreciate why Jay thinks a double conversion UPS will
*dam*, block, filter, or absorb a transient. He has no
numbers. Example: without numbers, the world will end soon.
Therefore start preparing for the end tomorrow. Tomorrow? I
did not provide any numbers. Why would you then assume I said
the world will end tomorrow? Numbers intentionally are not
provided so that you will make assumptions. Myth purveyors do
same to recommend a $500 double conversion UPS to only protect
one computer; to do what already exists inside the power
supply.

Jay misrepresents what was posted. In response to the line
filter inside a power supply, he said:
Maybe, but most often not. For the current to "pass through"
a filter, that filter must be composed (at least primarily) of
inductive components (i.e., a choke). But chokes are relatively
expensive and bulky;

Jay must damn well (should) know that a line filter is all
but required by FCC and other national regulations. A filter
(another layer of protection) that does contain inductive
components is found on minimally sufficient power supplies -
as existed even 30 years ago. Furthermore is his ignorance
about 30 years ago. Why was I was working with switching
power supplies he said did not exist? Jay did not know of
technology 30 years ago. And still Jay posts no technical
numbers.

Jay - I stand by what I have posted, cited the industry
standards that even existed 30 years ago, AND provided
numbers. Knowledge that comes from an engineering degree 30+
years ago when I worked on computers with such supplies while
building an 8080 computer, wire by wire, at home. A blunt
response to your smug insults about my knowledge. Apparently
I was doing this stuff before you were born. A point bluntly
directed at both your attitude and knowledge. Even worked
with a switching power supply cited in one of the famous 'Bill
and Dave' stories. But if you know so much, then you also
know of these legends. I doubt it. You even recommend a
plug-in UPS for hardware protection.

Your attempt to deny what existed 30 years ago is only the
tip of what could be an "I am young and therefore know
everything" attitude. Now for Jay's smoking gun
embarrassment.

Jay said:
A transformer has *nothing* to do with "galvanic isolation" ...
Excuse me! That alone says one is soaking wet behind the
ears. A repeatedly flawed summary of power supply functions -
including no knowledge of the required line filter - says
technical knowledge is not Jay. **Transformer provides
galvanic isolation**. Every lurker should recognize how
embarrassingly wrong Jay's sentence is. So wrong it must be
noted in multiple, consecutive sentences. Transformer
manufacturers provide numbers for that galvanic isolation.
But then Jay also tried to claim line filters don't exist in
power supplies - the chokes are too expensive and bulky? He
even tried to claim this stuff did not exist 30+ years ago.

Power supplies provide multiple layers of protection.
Layers that Jay denies - including the galvanic isolation
provided by a transformer. Note the "smoking gun" credibility
that also claims a plug-in UPS provides motherboard
protection.

For data blackout and brownout protection - all three types
of UPS are sufficient. A $500 version provides little more
than a $60 basic version. All include the same surge
protector circuit. And none provide additional motherboard
protection requested in the original post - the OP. Power
supply contains essential and standard protection functions.
A 'whole house' protector completes the protection 'system'.
As Jay has even demonstrated - double conversion UPSes on the
order of $500 still don't even provide (nor claim) effective
protection. Just the bypass wire that connects a destructive
transient directly to motherboard is a damning and
unchallenged fact.

Anything required by a computer is found in a 'basic'
UPSes. Other advantages such as "isolation between the load
and the line, true sine-wave output with minimal THD" are
made irrelevant since computer supplies, as even demanded in
Intel specs, make those expensive features unnecessary - a
waste of good cash.

Jay, your diatribe is a mix of curious knowledge mixed with
outright lies and technical incompetence. This 'PowerPoint'
knowledge is found in salesman for UPS manufacturers. Rather
curious that no respectable technician would post glaring
'smoking gun' errors as you have posted. Which UPS
manufacturer or distributor do you work for? Transformers
don't provide galvanic isolation? One cannot have basic
electrical knowledge and post such fundamental errors. Such
errors come from those educated in sales seminars. Even
electricians who need not understand that basic concept would
know better.

Folks - any protection provided by the $500 UPS is already
provided by computer's power supply that meets industry specs
of 30 years ago. 30 years ago: when I was working with and
designing stuff, and when Jay did not yet exist. Layers of
protection such as the standard line filter, galvanic
isolation in a transformer, full wave rectifiers, overvoltage
protector on output, etc all means even the high THD and noisy
outputs from a basic UPS create zero problems.

And again, notice again - Jay completely ignored the wire
that can carry a destructive transient right past all plug-in
UPSes and directly into motherboard. Funny how those who
recommend a UPS for protection routinely ignore that wire and
other facts - and don't post numbers.

Jay gets credit for posting one number - the switchover time
for a basic UPS. Typically 7 or 8 milliseconds - never more
than 10 msecs. Power supplies, as even required by industry
specs, must support a 100% load and still output power for up
to 16 milliseconds. That's a worst case number. In reality,
power supplies are nowhere near 100% loaded which means output
power remains much longer. But even at 16 millisecond, that is
*2 times* what is necessary. In direct opposition to claims
posted by others - switchover time even for the most basic UPS
is made completely irrelevant by all minimally acceptable
computer power supplies. So again, power supply has made all
those expensive UPS functions unnecessary - waste of good
money.

Any protection provided on a power cord is already inside
the power supply. Protection that requires a "$1 per
protected appliance" solution so that power supply will not be
overwhelmed by rare and destructive events. Others (ie using
a 'Powerpoint' technical education) would instead recommend
$500 solutions? How damning, again, a UPS recommendation made
without numbers.

So again we arrive at the bottom line for motherboard
protection. The fact that Jay (possible sales manager) avoids
discussing. Protection is defined by quality of and
connection to earth ground. Funny how Jay avoids that bypass
wire, claims a transformer provides no galvanic isolation, AND
avoids all discussion about earthing. Propaganda: lies by
telling half truths. They must avoid all discussion about
earthing to promote that UPS protection.

Jay T. Blocksom said:
Maybe for *your* computer(s), but certainly not for mine.

The el-cheapo standby-type supplies that "Mercury" (rather charitably)
described as "Basic" offer only minimal "protection" against the simplest (and
rarest) types of total power failures, and little else. They can do
absolutely nothing about the (often abysmal) *quality* of the power coming out
your wall outlet. Hence, their ability to shield the load from the plethora
of short-term fluctuations (so-called "brownouts", noise, frequency and
waveform aberrations, etc.) that have become increasingly common as power
utilities scrimp ever more on their QOS (and chronically fail to ensure that
generating capacity keeps pace with demand) is sorely lacking. The worst of
them also often throw all sorts of self-generated noise onto the line (and
into the air), which can (and does) interfere with the operation of *other*
equipment (especially RF-based equipment, such as a wireless LAN -- or your TV
set).
...

Only by the marketing mavens trying to sell then to the Great Unwashed, and
the gullible fools who have bought into their line of bull.
...

This is flat-out wrong.

A proper double-conversion UPS will offer MANY advantages over the various
low-end pieces. Among these are effective isolation between the load and the
line, true sine-wave output with minimal THD (sometimes also provided by the
better line-interactive units, but definitely not by the low-end standby
supplies you claim above to be "more than sufficient"), more robust batteries
and inverters (they _have_to_ be beefier, as they are in use all the time as
opposed to "just occasionally") and usually better build quality in general.

As for cost... Well, that can (and will) be all over the map, depending on
the manufacturer, the vendor, and especially the load capacity. You can spend
a few hundred, or you can spend several thousand -- but this also applies, to
very nearly the same degree, to standby & line-interactive models. As I
stated in my earlier article, a proper double-conversion UPS will generally
cost something on the order of 1.5-2X what an equivalent line-interactive
model will run. Here are a few examples for units in the 1KVA range (which
would be quite adequate for the OP's application):

TRIPP LITE OMNI SMART 1050VA
(Line Interactive / Stepped-square output) $277.95
<http://www.axiontech.com/prdt.php?item=34427&PRICECOMPARISONSID=7010b72b1aad24a0238d7ba547832d20>
TRIPP LITE SU1000XL
(Double Conversion / Sine-wave output) $413.95
<http://www.axiontech.com/prdt.php?item=61114&PRICECOMPARISONSID=7010b72b1aad24a0238d7ba547832d20>

The latter is exactly 1.489296636086 times as expensive as the former.

Para Systems Minuteman SmartSine S1000
(Line Interactive / Sine-wave output) $325.
<http://www.bisonbusiness.com/mis1fcoshcos.html>
Para Systems Minuteman MCP 1000 E
(Double Conversion / Sine-wave output) $525
<http://www.bisonbusiness.com/mimcfcoshcou.html>

The latter is exactly 1.615384615385 times as expensive as the former.

And finally, both from <http://www.battery-usa.com/Powercom-UPS.htm>:

PowerCom HOME-1000A
(Line Interactive / Sine-wave output) $281.33
PowerCom ULT-1000
(Double Conversion / Sine-wave output) $456.00

The latter is exactly 1.620872285217 times as expensive as the former.

Please note that I am *NOT* specifically recommending any of these particular
models, vendors, etc.; I'm just using them as handy examples.
...

You should take your own advice. Your description which follows is seriously
flawed in several ways (at least presuming you're talking about the typical
"switching" type PC power supply unit).
...

Maybe, but most often not. For the current to "pass through" a filter, that
filter must be composed (at least primarily) of inductive components (i.e., a
choke). But chokes are relatively expensive and bulky; and they don't do much
for you in a true AC environment. So typically, MOVs and bypass capacitors
are used instead. The current does not "pass through" these components (tho'
it might be said to "pass by" them).
...

Uhhh... no.

It is rectified, usually (or at least hopefully) by a full-wave bridge
rectifier circuit. This produces a (very rough and noisy) pseudo-DC output of
approximately 180V.
Virtually all noise, spikes, and surges are eliminated.
[snip]

Not even close!

Have you ever looked at the waveform output from one of those line-AC
rectifier circuits on a 'scope? I thought not. As noted above, at this stage
in the circuit, that waveform is *extremely* ragged and noisy (technically
referred to as "ripple") -- which is why the rectifier is (at least in any
half-decent supply) immediately followed up with more filtering caps (and
maybe even a small choke, this time, since the demands on it are so much less
after rectification).
...

It is disingenuous at best to call that a "layer of protection". It is simply
a necessary part any switching-type power supply. And the reasons for it are
not to provide any better protection or "power quality" to the load. The
near-sole reason for this type of design is *cost* -- you need a LOT less iron
to transform high-frequency (typically 5KHz to 50KHz) AC than low- (i.e.,
line-) frequency AC (60 Hz in the U.S.); and the cost savings provided by
using a relatively tiny transformer (see the next step in this saga) much more
than offset the costs of the "preliminary" rectification/switching circuitry.
It also makes for a physically smaller and lighter PSU, which saves still more
money in manufacturing and shipping costs down the line.
...

A transformer has *nothing* to do with "galvanic isolation", at least in this
context. And "galvanic isolation" in turn has *nothing* to do with protecting
a PC from power-line anomalies.

Do you even know what that term means? (Hint: Think corrosion. Or
batteries.)
...

Again, a simple rectifier circuit, which again produces a very rough and noisy
pseudo-DC output -- actually, several such rectifiers, producing several such
outputs, since the transformers used in PC PSUs necessarily have multiple
secondary windings/taps.
...

Well, of course -- we've just made a ton of noise and other crap via the
rectification process, which we now need to dispose of. But this is S.O.P.
for *any* power supply, switching or linear, in a PC application or virtually
anything else.
...

Uhhh... No, again. You are presumably referring to active voltage
regulation, which any decent PSU (for virtually any application, not just PCs)
will provide. But this is (at least typically) not so much a matter of
"overvoltage protection" (or under-voltage, for that matter) as it is a means
of enabling the designer to scrimp on the final filtering caps and/or chokes.
With an adequately responsive AVR circuit to rely on, those filtering caps
and/or chokes don't need to be nearly as effective as would be necessary if
they were being counted on to provide *all* of the output filtering; hence,
they can be smaller and cheaper.

In reality, the actual "over-voltage protection" feature provided by some PC
PSUs works *against* data integrity, not for it, since it can (and will,
if/when it trips) arbitrarily shut down the PSU (requiring a AC-off cold
start) without warning.
...

Thirty years ago, the "PC" had not yet been invented (tho' the first 8-bit
microprocessors had been developed, so the birth of the PC was imminent -- I
discount such "lunatic fringe" aberrations as the MITS Altair, which was
purely a hobbyist piece -- with a *linear* power supply, by the way), and
switching power supplies (in any application) were both relatively rare and
quite crude by today's standards. They were, quite justifiably, viewed as
rot-got el-cheapo substitutes for a "proper" linear power supply.

Yes, today's switching PSUs (at least the higher-quality ones) are much better
than those early travesties; but that's not the point.
...

Nonsense.

*IF* we could count on both the quality and the reliability of the AC mains
power we use to feed these supplies, at least most of them would do an
admirable job of running the mobos, memory, CPUs, disk drives, etc., that your
typical PC is composed of. But we *cannot* count on that. In fact, that
situation is getting worse every day, for the reasons already touched on above
(blame the NIMBYs, if you want; but the fact remains -- we are facing an
electrical power crisis that will surely only get worse before it gets
better). Concurrently, we are becoming more and more dependant on our
electronics -- especially our computer systems -- for our day-to-day
activities and existence. That is a prescription for a very unpleasant
wake-up call, which we *will* get, sooner or later; but I digress.

Getting back to the point...

The "hold-up time" specs quoted for typical PC PSUs range from about 10ms to
perhaps 17ms -- i.e., one AC cycle _at_best_ -- and even these are "best case"
specs obtained under laboratory conditions. All manner of power-line
aberrations (besides simple "total failures") will have event durations which
exceed this threshold. So some sort of "upstream" protection is
near-mandatory, if you value your data.

The "switching time" specs for typical low-end standby-type "UPS"s are in the
several-millisecond range (tho' again, these are "best case" lab-conditions
specs). Now, you might think that, because these figures are significantly
lower than (typically about 1/4 - 1/2) the typical PSU "hold-up time", there's
no problem... But you'd be wrong. This is only the actual *switching* time,
which by definition only starts *after* a power-line disruption has been
sensed and the control circuit tripped -- IOW, by the time the "UPS" *starts*
to switch the load, the crap has *already* been fed through to the output.
...

Ah, ha! Perhaps this explains (at least in part) your apparent fundamental
misunderstanding of the issues. It's not about "protection of computer
components", all of which are virtually always easily replaceable. It *is*
about protection of your DATA -- which in any serious application is far more
valuable than all the hardware, software, peripherals, etc., put together.
...

But here you imply that any ol' "plug-in UPS" is equivalent to any other
"plug-in UPS" -- which is most assuredly *NOT* the case. (And BTW... You're
also dead wrong about blackouts/brownouts not being able to harm hardware; and
I have the fried A/V gear from both my shore home and my main residence to
prove it.)

This raises the question of just what axe you're attempting to grind.

Out of curiosity, I just took a quick look at some of your other recent
postings via Google Groups; and I must say... Your grossly simplistic (and in
some cases just-plain-wrong -- such as was exemplified in
<http://groups.google.co.uk/[email protected]>;
hint: the voltage output of a regulated power supply will hold up just fine
until *immediately* before it falls apart spectacularly -- hence, your "cure
all" DMM tells you NOTHING about reserve capacity) views on matters related to
power supplies and your apparent obsession with PSUs as the root cause of all
computer problems (even those rather obviously caused by software or "pilot
error") seems suspect, at best.

No one here (least of all me) is claiming that a (presumably decent-quality)
switching-type standby "UPS" is totally worthless; but to suggest that they
are the end-all and be-all of UPS design is both misleading and just plain
silly.

--

Jay T. Blocksom
--------------------------------
Appropriate Technology, Inc.
usenet02[at]appropriate-tech.net

"They that can give up essential liberty to obtain a little temporary
safety deserve neither liberty nor safety."
-- Benjamin Franklin, Historical Review of Pennsylvania, 1759.
- - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - -
Unsolicited advertising sent to this domain is expressly prohibited under
47 USC S227 and State Law. Violators are subject to prosecution.
 
J

Jay T. Blocksom

w_tom said:
Recommend the $500 UPS to solve what a $1 per appliance
solution does? Again, even the green bypass wire makes the
"true online type" UPS ineffective. Destructive transient
bypasses the UPS. Just one of so many reasons why a plug-in
UPS is not effective.
[snip]
I'm pretty sure I remember you from a similar discussion 3 or 4 years back.
[snip]

After now seeing the later portions of the thread, it has become abundantly
clear that "w_tom" is a troll, subtype: frothing loon.
Serious questions: could you provide references, for those in the US 1)
that give a quantitative analysis of you r summary of plug-in
surge-protector performance? 2) That give a summary of whole-house surge
protection?
[snip]

I can't cite (or rather, am not willing to chase down at the moment) any
definitive references; but I can answer your question in broad terms.

Virtually all "plug-in surge-protectors" are based on Metal Oxide Varistors
(MOVs), sometimes bypassed by small capacitors (a few "high end" models also
include chokes in series with the AC lines; but these have become
exceptionally rare over the past several years, probably due to cost). MOVs
work sort of like a cross between a Zener diode and a resistor, by
absorbing/shunting current when a pre-defined "avalanche voltage" is exceeded.
They're cheap, and can react very quickly; so at first blush they seem to make
a good choice for this application -- except for one major Achilles's Heel:
They also share characteristics of both lightbulbs and fuses: IOW, they work
by gradually wearing themselves out (on the smaller spikes) or by silently
sacrificing themselves (for the larger spikes). The MOVs typically used in
"plug-in surge-protectors" start to clamp at around 165V, which is generally
"good enough" for most loads (IOW, most of the devices you would try to
"protect" with one of these things can inherently withstand at least that much
overvoltage, at least for some shortish period of time). And they will "live
through" surges of up to a few hundred volts or maybe even a few thousand
volts (as long as those surges don't last too long). But when a *really* big
spike (such as might be induced by a nearby lightning strike, or even a
particularly sloppy grid-switch by your power company) comes along, they
effectively go "poof*, and become open circuits -- and your "surge-protector"
is now simply an extension cord. Some of the better models of such "plug-in
surge-protectors" used to include one or more little neon lamps wired in such
a way that if/when the light goes out, you know the device has effectively
died. But this feature also seems to have dried up of late.

Now, in contrast to this, "whole-house surge protectors" come in two basic
flavors. Many of the more recently marketed models are essentially just
beefed-up versions of the MOV-based plug-in types. But the traditional
"whole-house surge protectors" (sometimes called "lightning arrestors") use a
completely different type of technology: basically a "spark gap". These units
are not subject to the foibles of the MOV-based units, and so will generally
last indefinitely; but they also cannot be effective against the "smaller"
spikes and surges that the MOV-based units take in stride.

Hence, the *best* solution is a combination of both types -- a "spark gap"
type suppressor hard-wired into your service panel (or, sometimes, the meter
box), *and* MOV-based surge suppressors at each critical point of use. The
former will help protect the latter, and the latter will help protect your
equipment. It's hardly a perfect solution; but it's probably the most
practical one.
Like others, I'm mainly interested in a UPS ability to switch to emergency
power when the grid goes down. The surge protection part of the UPS is
fairly cheap, comppared to the power protection.
[snip]

A decent UPS can do far more than that. It will also help ameliorate a wide
variety of other power-line ills, such as voltage sags, noise, weird frequency
aberrations, etc. -- all of which are becoming more common every day, for the
reasons I cited in my earlier f'up. But they should still be "fronted" with
at least a cheap MOV-based "surge suppressor", simply because it's easier and
cheaper to replace that when it dies than to repair the UPS if/when *its* MOVs
get fried.
I also surge-protect the
lines that go through my attic and connect distant PCs, because some have
the view that secondary induction of current in such lines is probably more
common than desttruction from direct lightning hits.

That probably depends at least in part on your specific situation; but I can't
see how it could hurt.

--

Jay T. Blocksom
--------------------------------
Appropriate Technology, Inc.
usenet02[at]appropriate-tech.net

"They that can give up essential liberty to obtain a little temporary
safety deserve neither liberty nor safety."
-- Benjamin Franklin, Historical Review of Pennsylvania, 1759.
- - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - -
Unsolicited advertising sent to this domain is expressly prohibited under
47 USC S227 and State Law. Violators are subject to prosecution.
 
J

Jay T. Blocksom

Correct. Double conversion would provide protection, but IF
a destructive transient was type of transient they claim to
protect from. A destructive longitudinal mode transient is
not seen by UPS battery and inverter as transient passes right
through UPS to damage computer.
[snip]

You are now spouting pure nonsense gibberish. For example: The term
"longitudinal mode transient" is utterly meaningless (at least in this
context).

Please resume your meds.

--

Jay T. Blocksom
--------------------------------
Appropriate Technology, Inc.
usenet02[at]appropriate-tech.net

"They that can give up essential liberty to obtain a little temporary
safety deserve neither liberty nor safety."
-- Benjamin Franklin, Historical Review of Pennsylvania, 1759.
- - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - - -
Unsolicited advertising sent to this domain is expressly prohibited under
47 USC S227 and State Law. Violators are subject to prosecution.
 
W

w_tom

Jay notes that MOVs do degrade with use. And then we apply
the numbers he forgot. A typical plug-in UPS may be only 345
joules. It will use up to 230 joules and sometimes only as
little as 115 joules during the transient. Let's say this
protector can survive two 'same size' transients. Therefore,
even a minimally sized 1000 joule 'whole house' protector
(also described as the $1 per protected appliance solution),
will withstand on the order of 300+ same sized surges. 300
verses 2? As joules increase, protector life expectancy
increases exponentially. This made obvious from MOV
manufacturer data sheets - the numbers. What does Jay
routinely forget to provide? The numbers.

Why not increase joules inside that UPS? They are not
providing effective protection. Obviously - no earth ground.
They only claim to provide some protection. Near zero
protection is enough to claim protection.

Once we apply numbers, then MOV degradation is a problem
only in undersized protectors (ie plug-in UPS and power
strip). If the MOV goes "poof* , well that protector was
so grossly undersized as to abandon transistors to a
transient. "Poof* means a grossly undersized and totally
ineffective protector. Ineffective protectors (power strip
and UPS) are made obvious by undersized MOVs - too few joules.

MOVs (properly sized) degrade in normal use. MOVs
vaporize when the grossly undersized. PC Magazine noted these
serious safety problems in two issues in the 1980s. Fires
from insufficiently sized power strip protectors created a
safety standard - UL1449. A protector can completely fail -
provide no protection during certification - and still get the
UL1449 approval rating. Others will imply that UL1449 means
effective transistor protection. It does not. UL is only
concerned that human life is protected.

The UPS will "ameliorate a wide variety of other power-line
ills, such as voltage sags, noise, weird frequency
aberrations, etc. -" And then we again apply spec numbers
from Intel. Power supply design makes all those 'ills'
irrelevant. Weird frequency aberrations? That is a
salesman's expression. In the meantime, power supply that
work on 60 Hz power also works when frequency drop to and
below 50 hertz. Where is the beef? What noise? Power supply
contain line filters to meet FCC regulations that make noise
irrelevant. Line filters that Jay said do not exist.
Furthermore, noise does not cause hardware damage. Voltage
sags? Incandescant lamps must drop to 40% intensity and still
a power supply must provide 100% power. This demanded by
numbers in Intel specs for computer power supplies. None of
these 'ills' are destructive to hardware. So what does that
$500 UPS provide?

Jay is demonstrating salesman sophistication using words
like 'weird frequency aberrations" that have no engineering
meaning. "Ameliorate" that makes him sound educated. And yet
still he provides no numbers.

A UPS will not protect the Original Poster's motherboard.
But it does "ameliorate weird frequency aberrations"? Well,
yes. If you buy the $500 UPS. The typically plug-in UPS for
$100 does not "ameliorate" and does protect data from
blackouts and brownouts. Protecting data is why we install a
plug-in UPS.
 
W

w_tom

Jay - who claims transformers provide no galvanic isolation
- also denies the longitudinal mode transient. He must avoid
discussing the various types of transients to promote myths.
Longitudinal mode transients damage hardware. A most famous
longitudinal mode transient is lightning. But Jay tells us is
does not exist? Clearly he must know. He posts no numbers.

Other damning facts that Jay must avoid. He ignored the
wire that carries a destructive transient around the UPS and
into motherboard. He avoids mentioning those pathetically
undersized MOVs that are the surge protection circuit in
UPSes. And most damning of all, he still avoids any
discussion about earthing. Protection is about earthing as
even Franklin demonstrated in 1752. So Jay must avoid earthing
discussions. Those plug-in UPSes have no effective earthing.
No earth ground means no effective protection. So Jay instead
denies longitudinal mode transients - an electrical concept
taught to first year engineering students.

Jay's technical knowledge is symptomatic of what is taught
in salesmen seminars. Often referred to elsewhere as a
"PowerPoint" education. "A transformer has *nothing* to do
with "galvanic isolation", ..." would never be posted by the
technically educated. His is salesman science.

Others are cautioned about 'experts' who can't post
numbers. No numbers means junk science reasoning. The
'smoking gun' - that transformers don't provide galvanic
isolation - says Jay has insufficient technical knowledge.
This is first year EE stuff. Instead he posts classic
salesman propaganda. Reality: a UPS provides no useful
motherboard protection. It claims to do what already exists
inside the power supply.

Meanwhile a transformer is installed in all electronic
appliances that require galvanic isolation so that the user
does not get electrocuted by AC mains. Why? Jay tells us
that transformers don't provide this isolation. But then he
just knows a $500 UPS will protect a motherboard - without
that essential connection to earth ground. No earth ground
means no effective protection. UPS will ignore this fact to
claim protection from transients that don't typically do the
damage.
 