Guest
Posts: n/a
|
I'm trying to decide what rackable UPS to buy.
So I have a Poweredge 2850 with redundant power supplies. It says the power supply is rated at 700W. Does this mean because I have redundant power my server is actually drawing 1400W while in use? If so, what kind of UPS should I get? Does this mean I need a 1430W / 2200VA UPS? If I got a 480W UPS is that too small? How do I know? I'll have a small switch and a firewall on it too. Thanks. |
|
|
|
#2 |
|
Guest
Posts: n/a
|
Normally redundant means "back-up". So if you have a 700 Watt supply
for your server and a redundant one, than your using [or have] 700 watts. The other supply is off until the first one fails. If both supplies were operating full-up ~ what is redundant? The back of the unit should indicate the power draw. Look at the power drain for each unit, add them, add some margin [10%] and get a unit that supports that number. www.interfacebus.com |
|
|
|
#3 |
|
Guest
Posts: n/a
|
On Mon, 02 Jan 2006 02:31:58 GMT, kenw232@yahoo.com (Ken
Williams) wrote: >I'm trying to decide what rackable UPS to buy. > >So I have a Poweredge 2850 with redundant power supplies. It says the power >supply is rated at 700W. Does this mean because I have redundant power my >server is actually drawing 1400W while in use? If you link to the specs, manufacturer product and parts page it might help. Generally speaking (considering the class of system) it is very unlikely you have 2 x 700W PSU in it, more likely 2 x 350W PSU. That means the system "could" run entirely off of one 350W PSU, thus the redundancy aspect of it, that if one psu failed it would keep running off the other one. That only means the system uses LESS than the 350W the PSU can provide. For example, if you have a 20 gallon gas tank, it doesn't mean you use 20 gallons driving to work, necessarily, only that it was enough gas to get you where you needed to go. A random guess would be that the system uses roughly 250W, a little more or less depending on load and # of drives. There is further variability though, in what else needs powered along with it, like a monitor or switch or (not). Such is the case with servers- sometimes put on their own supplies and other times a larger UPS network that handles other equipment too. >If so, what kind of UPS should I get? Does this mean I need a 1430W / 2200VA >UPS? No, the power supply itself can be mostly ignored for the purposes of factoring UPS capacity. > If I got a 480W UPS is that too small? If you mean 500VA, and in a consumer-grade unit, yes that's cutting it too close- it'll probably work, but for a server that is too little margin. >How do I know? I'll have a >small switch and a firewall on it too. We can't know what your switch and firewall consume, but typical _modern_ standalone units are relatively low power consumers, maybe 25W total. What is the strategy for the UPS? Is it meant to keep system running during an outtage? If so, you may need a much much larger unit. If it's only needed to allow system to survive momentary power "flickering" or shut off gracefully in event of a full outtage, then all it needs do is support the current, VA the system requires. In this case, a 700VA UPS would be about minimum as it's good to factor for double the actual estimated wattage of the unit (250W above). On a high-end commercial UPS, there may be less fudging involved, rather than 2 X you might get away with 1.25-1.5X that 250W, but in the end it is a more expensive UPS too, so either way it can be a factor of what the budget is. Given the other devices too, it might be nice to aim at 1000VA and AVR (online voltage regulation). If you have different needs for the server and for the switch or firewall, for example if they're connected to different equipment not all of which is succeptible to same power grid outtages, alternate UPS or generator, etc, it might make sense to put the switch and firewall together on a different UPS than the server, as those two might run for multiple times as long alone on an UPS, while the server will not run for over an hour without the UPS becoming costly. Define the needed runtime per each device, weighed against the budget for the UPS. The generic answer for powering all 3 is 1000VA, 700VA if budget is tight for them to run long enough to shut down gracefully, less than 1/2 hour runtime. |
|
|
|
#4 |
|
Guest
Posts: n/a
|
On Mon, 02 Jan 2006 02:31:58 GMT, kenw232@yahoo.com (Ken Williams)
wrote: >I'm trying to decide what rackable UPS to buy. > >So I have a Poweredge 2850 with redundant power supplies. It says the power >supply is rated at 700W. Does this mean because I have redundant power my >server is actually drawing 1400W while in use? No. >If so, what kind of UPS should I get? Does this mean I need a 1430W / 2200VA >UPS? If I got a 480W UPS is that too small? How do I know? I'll have a >small switch and a firewall on it too. You need to determine actual power draw and the run time you need. You can determine maximal & minimal watts from specs & use that to calculate your runtime needs. Or a handy tool to have anyway is the Kill A WATT meter http://www.p3international.com/prod...0/P4400-CE.html (Or something similar). The advantage is you can quickly & easily see what the total draw really is on startup, idle, & load, and "average use". This is faster & potentially more accurate. With a push of a button you can get real VA (which is how UPSs are typically sold). You won't use it very long to make this purchase decision, but it is an inexpensive tool that can be quite handy to have around (IMHO). |
|
![]() |
|